While it's not a JK electrical question, I wasn't sure where to post it, and besides, i'll be using the welder for the jeep.

I have a miller mig welder. 230V 20 amps single phase. My garage has a full panel with plenty of slots and amps to spare.

I plan on putting a receptcle a few feet away from the panel for the welder, plan on using 10 gauge wire, a 50 amp recepticle and a 30 amp breaker (while the welder is rated at 20 amps it has a 50 amp 3 prong plug) does this sound good so far?

At the panel I'll need to use two breakers, one for the black one for the red wires, do I use two 30 amp breakers or two 15 amp breakers (30 amps total)? With the white wire to the neutral and the bare ground wire to the ground strap!

Does this sound correct, or do I have it ass backwards?
 

·
Registered
Joined
·
120 Posts
You need to use a 30 duplex breaker for your red and black wires. You want both circuits disconnected if one side trips.
 

·
Registered
Joined
·
1,466 Posts
If you are not sure what you are doing call an electrician! It won't cost that much for one to hook that up for you and your house won't burn down! That is my PSA for you.

With that said, a 30 Amp breaker will be two 15 amp breakers with one pull switch (the circuit will trip both breakers at once and you cannot reset individual breakers).

Your gauge of wire really should be 8 gauge not 10 for 50 Amp service.

The white wire will be connected to the buss bar (more than likely where the other white wires are).

Why are you using a 50 amp recepticle on a 30 amp breaker?

Again call an electrician if you have any doubt. 220v is no joke and can burna panel rathr quickly if wired wrong.
 

·
Registered
Joined
·
353 Posts
i is an electrician and to be legal for 20 amps all you need is romex 12/2 and a 20amp 2pole breaker it is that easy
black/white go to breaker and the ground to ground bar in the panel and wire in your receptical that matches your plug
on your welder probably 2 flat prongs and the normal ground on the bottom hope this helps
 

·
Registered
Joined
·
353 Posts
there is no neutral in a 220 volt welder you can tape the white wire red or blue but you dont need a neutral there is only 2 hots and a ground
 

·
Registered
Joined
·
494 Posts
10 Gauge wire is fine if you have a 30 amp breaker. The breaker you need will have two switches tied together and will say 30 on the handle. Check to see what a 50 amp receptacle costs versus a 30 amp receptacle and a new 30 amp plug.
 

·
Registered
Joined
·
124 Posts
there is no neutral in a 220 volt welder you can tape the white wire red or blue but you dont need a neutral there is only 2 hots and a ground
You just made my point. You are using the ground as your neutral return. The ground conductor on most 12/2 romex is not 12AWG either.

No offense intended, but that's kind of rigged.

To the OP, it will be a few dollars difference for 10/3 wire, why skimp and have to re-code wires and shit when you can just have peace of mind. Run the neutral-white properly and ground the outlet box. You said this outlet is close to the box, the wire isn't going to cost much (100feet of 8/3 now THAT'S spending money!)
 

·
Registered
Joined
·
126 Posts
You just made my point. You are using the ground as your neutral return. The ground conductor on most 12/2 romex is not 12AWG either.

No offense intended, but that's kind of rigged.

To the OP, it will be a few dollars difference for 10/3 wire, why skimp and have to re-code wires and shit when you can just have peace of mind. Run the neutral-white properly and ground the outlet box. You said this outlet is close to the box, the wire isn't going to cost much (100feet of 8/3 now THAT'S spending money!)
I is a "MASTER" electrician. If the equipment requires a 20 amp circuit. Then that is all you are required to install. 20 amp = #12 awg and 30 amp = #10 awg. Installing bigger wire is a waste of money. Installing bigger breaker risks burning down your new equipment. Yes you do need a two pole breaker for 220 / 240 volt equipment. If it is a 4 wire connection then you will need a neutral wire. If it is a 3 wire conection then you only need a ground.
 